Seeing this thread pop up and it's hitting close to home — I've been wrestling with something very similar in my shepherd's hut setup for the past few weeks.
Running a Victron Multiplus 24/800 with a Cerbo GX, SmartShunt, and MPPT 100/20, paired with a Fogstar 24V 100Ah LiFePO4 (the one with integrated BMS, no external CAN management). Intermittent low battery warnings keep appearing in VRM despite the state of charge reading as perfectly healthy at the time.
A few things I've narrowed it down to:
- BMS communication gap — without proper battery management protocol (no DVCC handshake), the Multiplus is relying purely on voltage thresholds. A momentary sag under load can trip the warning even if capacity is fine
- DC cable sizing — I initially underestimated voltage drop on my 24V bus. Worth measuring actual terminal voltage under load rather than trusting the shunt reading alone
- Low battery restart/shutdown thresholds in VEConfigure** — these are often set conservatively from factory and worth reviewing against your actual battery spec
What I haven't fully resolved is whether the integrated BMS on these batteries is occasionally causing a brief current interruption that the Multiplus interprets as low voltage. Has anyone else seen this with similar setups?
Would be curious whether those of you running Renogy or other batteries with standalone BMS boards have had cleaner results. Also whether tweaking the ESS assistant settings made any difference for anyone running grid-tied configurations.