Ran into something similar last autumn when I was commissioning the shepherd's hut system — worth sharing here because it's a genuinely tricky edge case with Victron kit.
I had a Multiplus-II 3000 acting as the primary inverter/charger alongside a secondary unit, fed by a Honda generator when solar input dropped off during the darker months. The issue was that the MP-II kept pulling the generator into an unstable load condition — not quite overloading it, but hovering right at that awkward threshold where the generator hunts for frequency.
After a lot of head-scratching and digging through Victron's ESS documentation, I realised the problem was the PowerControl current limiter wasn't playing nicely with the battery absorption phase. The Multiplus was essentially trying to push full charge current and supply loads simultaneously, with no headroom left for the generator to breathe.
The fix that worked for me:
- Set the AC input current limit conservatively in VE.Configure (I dropped to about 80% of the genny's rated output)
- Enabled dynamic current limiting so the MP-II backs off gracefully under fluctuating load
- Tweaked the absorption voltage slightly lower on the Fogstar lithium cells to reduce peak charge demand
It's been solid since. But I'm curious — for those running multiple Multis in parallel with a supplementary charger unit thrown in, are you using ESS or a straight VE.Bus setup? I suspect the spinning reserve issue becomes significantly more complex when you've got three units negotiating simultaneously. Anyone actually measured the AC coupling behaviour in that configuration with a proper power analyser?