Got a head-scratcher on my narrowboat setup and wondering if anyone's wrestled with this beast before.
Running a MultiPlus-II 4k5 paired with a single Dyness DL5.0C Pro (51.2 V / 100 Ah) and a Victron SmartSolar MPPT 150/45, all configured as an ESS — or at least it was ESS until I decided canal life meant I'd rather go full off-grid and stop relying on marina hookups entirely.
The problem: the moment shore power drops (whether I unplug intentionally or the marina supply wobbles — and blimey, it wobbles), the MultiPlus throws a Low Battery alarm almost instantly, then a High DC Ripple warning follows within seconds, and the whole inverter shuts down. Boat goes dark. Kettle dies mid-brew. Tragedy.
Battery is sitting at a perfectly healthy state of charge — we're talking 80%+ — so it's not actually low. My suspicion is that the single Dyness unit can't handle the instantaneous current demand when the MultiPlus switches from grid-assisted to standalone inverting, causing a voltage sag that the MultiPlus misreads as a dying battery, with ripple spiking because the BMS is momentarily current-limiting.
Questions for the collective wisdom of this forum:
- Is one 100 Ah LiFePO4 just fundamentally undersized for a 4k5 inverter in standalone mode?
- Should I be looking at the charge current settings or the AC input current limit in VEConfigure?
- Anyone had luck with the ESS Assistant vs pure off-grid config making a difference here