Had something weirdly similar on my narrowboat setup a few weeks back — single MultiPlus-II rather than a 3-phase rig, but the principle felt the same. Brief total dropout, everything killed for maybe 2-3 seconds, then back up as if nothing happened. VRM showed absolutely nothing. No warnings, no alarms, no blip in the SOC graph that would explain it.
Took me ages to even convince myself it had actually happened and wasn't just me imagining things.
My working theory at the time was a brief BMS disconnect — my Fogstar cells have a Daly BMS and I've read others saying a momentary BMS protection trip can cut the DC side faster than the MultiPlus can log anything meaningful. By the time it's recovered, there's nothing to write home about in the event log.
A few things worth checking if others are seeing this:
- DC cable connections — especially ring terminals under vibration (more relevant on a boat, fair enough)
- BMS communication timeout settings — if you're on VE.Can or even just the two-wire assistant, a hiccup there can cause a controlled shutdown
- AC input quality — even with AC-Out configurations, a weird grid blip can sometimes trigger a transfer that looks like a blackout from inside the property
Has anyone on a static cabin or house setup with a 3-phase arrangement seen this? Curious whether it's more likely to show up on larger installations where the phases have to stay in sync. Feels like there's something subtle going on that Victron's logging just doesn't catch at the right resolution.