Interesting timing on this thread — I've been chasing something very similar with my Multiplus II 3000 setup on the narrowboat.
Mine's a slightly different config (no AC coupling, just Fogstar Drift lithium and a Cerbo GX), but I've noticed that after a shore power disconnect — whether deliberate or a genuine supply drop — there's sometimes a noticeable delay before the unit picks up inverting duties. Most of the time it's fine, but occasionally it just... sits there. The Cerbo shows the grid as gone but the inverter stays in a kind of limbo state rather than switching over immediately.
A few things I've already checked:
- Transfer switch delay — adjusted in VEConfig, currently at the default 50ms
- Grid code settings — set to G98 (UK), wondering if this is too cautious for my situation
- AC input current limit — doesn't seem relevant here but checked anyway
My suspicion is it might be related to the grid code frequency/voltage tolerances being overly sensitive, causing it to detect a "fault" rather than a clean disconnect, which perhaps changes how it recovers?
Has anyone else in a UK setup had this with G98 or G99 configured? I'm particularly curious whether switching to a less restrictive grid code (for off-grid / backup use where you're not actually exporting) resolves it.
Also — does anyone know if this behaviour changed in recent firmware? I'm on v502 on the Multiplus II.
Would be good to hear from anyone running AC-coupled setups too, as the original scenario sounds like the Huawei inverter might be complicating the handoff further.