Sounds like a cable sizing issue more than anything else. Inverters are notorious for pulling massive surge currents at startup — even a modest 1000W unit can spike well beyond what the steady-state draw would suggest.
Few things worth checking:
- What gauge are your battery-to-inverter cables? Most narrowboat installs I've seen use undersized cable because people go off the continuous rating rather than peak. You want to be generous here — 70mm² minimum for anything over 1000W, ideally 95mm²
- Where's the fuse/breaker sitting in the circuit? If it's right at the inverter rather than at the battery, you're potentially protecting the wrong thing
- What inverter did you go for? Modified sine wave units can be particularly spiky at startup
My garden office setup had similar gremlins when I first wired in a Victron Phoenix — kept nuking the breaker every time the compressor fridge kicked in. Turned out my cable run was just long enough to cause enough voltage drop that the inverter was compensating hard on startup.
On a narrowboat the cable runs are usually shorter, which is a point in your favour, but the marine environment adds its own complications — any corrosion on terminals will add resistance and make the problem worse.
Worth getting a clamp meter on those cables if you can and logging the actual startup surge. Might tell you exactly where the weak point is.
What's the battery bank — lithium or lead acid? That changes things quite a bit in terms of how the BMS might be interacting with sudden load spikes.