Been down a similar rabbit hole recently, planning a three-phase setup for a static caravan site project — so this topic is very much on my radar.
The Victron three-phase ESS route is genuinely impressive once it all talks to each other, but I've learned a few things the hard way with smaller single-phase builds that I reckon scale up:
- Cerbo GX configuration takes patience. Getting the grid code right for UK G98/G99 compliance isn't always obvious, especially once you add a generator into the mix with ATS
- Pylontech and Victron comms are generally solid, but with larger battery stacks like the UF5000s, double-check your DVCC settings — I had some odd balancing behaviour on a Fogstar/Victron hybrid setup until I sorted that
- MPPT RS sizing — are you running these in parallel arrays? Curious what your PV layout looks like and whether you're hitting any shading issues that might skew the phases unevenly
The diesel generator handover is probably where I'd want the most confidence. What ATS are you using? I've seen a few installs where the transfer time caused the MultiPlus units to briefly drop to inverter mode before re-syncing, which on a commercial-ish load is less than ideal.
Anyone else here running a full 30 kW three-phase Victron ESS in the UK? Would love to know how you've handled DNO notification paperwork — that feels like its own adventure with anything above 16A per phase.