Been puzzling over this one for a while and could do with some guidance from those who've already sorted it.
My setup is a static caravan with a Victron MultiPlus-II as the inverter/charger, Fogstar Drift lithium batteries, and a separate consumer unit feeding several circuits. I've got both off-grid solar running day-to-day and occasional shore power hook-up for top-up charging.
The question I keep coming back to is around earthing at the DC/AC boundary — specifically whether the neutral should be bonded to earth on the inverter's AC output side, or whether it's better to let the system float.
From what I understand:
- A floating system can make fault detection harder, since a single fault to earth won't necessarily trip an RCD
- Bonding neutral-to-earth at the inverter output creates a proper reference, allowing RCDs downstream to function as intended
- But if you're ever switching between off-grid and shore power, having two neutral-earth bonds simultaneously is apparently a problem
My MultiPlus has an internal transfer switch, so when shore power is present it passes through — does that mean I should only bond at the inverter output when running off-grid, and rely on the DNO supply's own earth reference when on hook-up?
Has anyone used an external relay or the Victron assistant to switch the bond in and out automatically depending on which source is active? I'd rather not have this as a manual step I might forget.
Also wondering if there are any specific UK regs considerations (BS 7671 / 18th Edition) that affect how this should be handled differently to, say, US-based advice which seems to dominate most of the online resources.