Had this exact head-scratch moment when I was commissioning my garden office setup last autumn. Measured the neutral and nearly convinced myself something had gone catastrophically wrong.
Short answer — yes, it's generally normal on a floating neutral inverter, which most Deye units are. The neutral isn't bonded to earth internally, so you'll often see a phantom voltage reading (sometimes 50-60V AC) that disappears the moment you put any meaningful load on it. It's the high impedance of your multimeter essentially "picking up" the midpoint of the AC waveform rather than a true fault voltage.
The fix most people go for is a neutral-to-earth bond at the first point of distribution — so your consumer unit or isolator. One short cable between neutral bar and earth bar. Job done, reading drops to near zero.
That said, a few things worth checking before you assume it's just floating neutral weirdness:
- Which Deye model are you running? Some of the hybrid units behave differently to the standalone inverters
- Are you grid-tied or fully off-grid? Grid-tie changes the bonding situation considerably
- What's the actual voltage reading you're seeing — and does it shift under load?
The Victron crowd tend to be more opinionated about this than Deye users, but the underlying principle is the same across most sine wave inverters.
Would be curious whether others here have bonded theirs permanently or used a relay-switched bond to handle generator input switching — that's the rabbit hole I nearly fell down before keeping things simple.