Been down this exact rabbit hole with my narrowboat setup, so this might save someone a headache.
When I first got my Victron MultiPlus-II talking to the Pylontech US5000s, I had the same maddening situation — batteries showing full, panels throwing out decent output, and the inverter still insisting on pulling from the shore power hookup at the marina.
The culprit for me was the ESS Assistant. It's designed for grid-tied systems where you want to offset mains usage — brilliant for a house in Spain apparently, not so brilliant when you're genuinely off-grid or just want to run entirely from solar and batteries.
A few things worth checking if you're in a similar spot:
- ESS vs Off-Grid mode — ESS assumes a grid connection is desirable. If you're truly off-grid, you might not want ESS installed at all
- Grid setpoint — even with batteries full, ESS can be configured to maintain a small grid draw; worth checking that value in VEConfigure
- "External Control" on the inverter display — this usually means ESS or DVCC is managing it, not a fault as such, just the assistant taking the wheel
- DVCC settings — if Pylontech BMS is talking to the Cerbo/CCGX, make sure CVL and CCL values are coming through correctly
On the narrowboat I ended up ditching ESS entirely and running in inverter-only mode with the MultiPlus set to ignore the landline unless batteries drop below a threshold. Much cleaner behaviour.
Anyone else running Pylontechs with a MultiPlus-II in a genuinely off-grid setup? Curious whether others have found ESS