Had this exact issue with a cheaper inverter a while back — not Giandel specifically but same sort of unit. The OL (overload) fault with nothing connected is almost always one of a few things:
1. Internal fault on startup
Some inverters will throw OL if there's a problem with the internal circuitry — a failed capacitor or MOSFET can cause it to read a phantom load.
2. Low battery voltage
What's your battery voltage sitting at when it triggers? If the 12v bank is sagging below ~10.5v under the inverter's own startup draw, some units misread that as an overload condition rather than a low voltage fault. Worth checking with a multimeter directly at the terminals.
3. Dodgy connection
Loose or undersized cable between battery and inverter can cause a voltage drop that confuses the unit. What cable gauge are you running? For a 3000W inverter you really want 70mm² minimum, ideally with the shortest run possible.
I'd try:
- Fully charge the battery first
- Check all connections are tight and correct gauge
- Do a factory reset if the unit has one (hold the power button sequence — check the manual)
If it's still doing it after all that, the unit itself may be faulty. Giandel's warranty support can be a bit hit and miss depending on where you bought it from.
What battery setup are you running — lead acid or lithium? And is this a new unit or has it worked previously? That'll narrow it down quite a bit. Others on here may have had direct Giandel experience too, be curious what they say.