Had something similar crop up on my narrowboat setup last winter and it genuinely had me scratching my head for a good few days.
Running a Victron Phoenix 24V/3000VA and kept getting low battery alarms despite the bank sitting at a perfectly healthy 26–27V on the display. Everything looked fine but the inverter was having none of it.
Turned out the culprit was voltage sag under load. The resting voltage read great, but the moment I kicked on anything substantial — the induction hob, even the kettle — the voltage was dipping sharply at the battery terminals for a fraction of a second. Not long enough to show clearly on a basic meter reading, but enough to spook the inverter.
A few things worth checking if you're seeing the same:
- Cable sizing — undersized cables between the battery and inverter will cause sag under load. I had to upgrade mine to 70mm² before things settled
- Battery connections — a loose terminal can cause momentary resistance spikes that look fine until load hits
- State of charge vs resting voltage — 26V on a 24V LiFePO4 can still mean a fairly depleted cell if you've not let it rest properly after charging
- BMS cutoffs — if you're running a Fogstar or similar lithium bank, check whether the BMS is sending a signal to the Victron via VE.Bus
The Victron Connect app really helped me dig into the historical data and spot the sag pattern. Without it I'd still be puzzled.
Anyone else had this? Curious whether it's more common on older lead-acid setups or whether lithium users are hitting it too.