Been through this exact planning phase myself before fitting my MultiPlus-II 48/5000/70 in the motorhome, and the wiring diagram stage is where most people make costly mistakes before a single cable is run.
The bit that catches people out with the 48/3000/35 specifically is the AC input current limit — that 35A figure is the charger rating, not the inverter output ceiling. If you're planning to use shore power or a generator as your AC-in source alongside solar buffering, you need to think carefully about how VE.Bus is going to arbitrate between them under varying load.
A few things worth pinning down before you commit to your cable runs:
- Battery cable lengths — keep them equal and as short as physically possible. Voltage drop at 48V hurts less than at 12V, but it still matters under high inverter load
- Are you running ESS or just Inverter/Charger mode? ESS with a grid meter changes everything about how the system responds
- CT clamp placement — if you're measuring grid input for self-consumption optimisation, where that clamp sits relative to your main incomer matters enormously
- Fogstar or similar LiFePO4? Make sure your BMS DVCC settings are properly configured in VEConfigure before you energise anything
The Victron documentation is genuinely excellent but it assumes a lot of background knowledge. The Victron Community is worth cross-referencing alongside here.
What's your battery bank setup and are you planning full ESS or standalone? That'll change the advice significantly.