Been down this rabbit hole myself on the narrowboat, so a few things worth checking before anyone signs off on this as "good to go":
The obvious one — what's your cable sizing between the battery bank and inverter? A 3000W inverter at 48V is pulling around 62.5A continuous, but at startup/surge you could easily see 2-3x that. Undersized cables will cause voltage drop, nuisance tripping, and in a worst case, heat you really don't want near a battery bank.
Fusing — is there a fuse or MEGAFUSE within 300mm of the positive battery terminal? Non-negotiable in my view. ANL or MEGA type, appropriately rated.
What batteries are you actually running? Fogstar Drift cells, a pre-built LiFePO4 pack, lead acid? Makes a big difference to how the system should be configured, particularly if your inverter/charger is a Victron Multiplus — the charge profile needs to match.
BMS comms — if you've got lithium, is the BMS talking to the inverter? Without that link, you're relying entirely on the BMS to hard-disconnect under fault conditions rather than the inverter backing off gracefully. Fine as a fallback, not ideal as the primary protection.
Post your actual schematic or at least a parts list and someone here will give you a proper steer. There's a lot of "looks fine" systems on this forum that aren't fine once you dig into the details.