Had a similar nightmare with a PowMr unit in my van build last year. The grid failover logic on these cheaper hybrid inverters is genuinely sketchy — it's like the firmware assumes you'll always have a healthy battery present and just throws a wobbly when it doesn't.
A few things worth checking:
- Battery voltage threshold settings — some PowMr models have a "back to grid" voltage parameter buried in the settings menu (often labelled something like "battery low voltage" or "utility charge"). Make sure this is set above your actual low-voltage cutoff so it triggers in time.
- Battery disconnect scenario — this is the bigger issue IMO. A lot of these units won't switch to grid cleanly if the BMS disconnects the battery, because they're expecting the battery to act as a buffer during the switchover. Victron handles this much more gracefully, unsurprisingly.
- Firmware version — PowMr have pushed updates that address failover behaviour. Worth checking their website or contacting them directly, though their support is... variable.
Longer term, if you're serious about reliability, it might be worth adding a small buffer battery that stays connected even when the main pack cuts out — just enough to keep the inverter's logic board happy during the transition.
What model specifically are you running? The 5kW and 3.5kW variants seem to behave differently in my experience. Also, is this a fixed installation or a vehicle setup? Makes a difference in terms of what workarounds are practical.
Keen to hear what others have found — this feels like it should be a more widely discussed issue than it is.