Interesting thread — following with curiosity because I nearly went down the PowMr route before settling on a Victron setup for my shepherd's hut.
The 120V spec is a bit of an oddity for us UK folks (wondering if this is a US-spec unit being run differently?), but the underlying issue of an inverter not seeing panels is pretty universal and I've seen it crop up with a few of the Chinese all-in-ones.
A few things worth checking if you haven't already:
- PV input voltage at the unit itself — not just at the panels. Voltage drop across dodgy MC4 connectors can cause the controller to simply not register the source
- VOC vs MPPT input range — some of these units have a narrower input window than advertised, particularly on the lower end. Worth cross-referencing your panel's VOC against the actual MPPT spec in the manual rather than the marketing blurb
- Earth/ground configuration — I had a bizarre fault on my van conversion Renogy setup once that turned out to be a floating ground causing the controller to behave erratically
What panels are you running and how are they wired — series, parallel, or mixed? That'll probably narrow it down quickly. Also, what's the VOC showing on a multimeter directly at the PV terminals on the unit?
Glad you've finally got it powered up though — that moment when everything clicks on for the first time is genuinely brilliant. Would love to hear what your first day of solar harvest looks like once it's properly sorted.