Had a similar headache last year with my Victron Multiplus-II and a cheap diesel genny — worth sharing in case others are going through the same.
The generator I was using (a Hyundai 6.5kW, no AVR) was throwing out voltage that wandered all over the place under load — sometimes dipping to 205V, occasionally spiking past 250V. The Multiplus just flatly refused to accept it as a valid AC source. Frustrating doesn't cover it.
What eventually sorted it:
- Lowering the AC input low limit in VEConfig — I dropped mine to 180V as a starting point
- Disabling UPS mode — this made a huge difference, the Multiplus became much less fussy about transfer timing
- Increasing the AC input current limit gradually to avoid overloading the genny on startup
I didn't mess with country settings personally, but I've seen posts on the Victron Community forum where people running non-AVR generators in the UK have changed the frequency acceptance range slightly. Worth reading through if you're still stuck.
One thing I'd genuinely recommend — if your generator is running without an AVR and you're regularly relying on it for backup, just get an AVR-equipped machine. The Fogo units people mention seem decent but I can't speak from direct experience. Hyundai, Stephill, and Honda EU series all behave much more predictably with inverter-chargers in my experience.
Anyone else found specific VEConfig settings that work well with AVR-less generators in a UK setup? Curious whether the country standard tweak actually helps or just masks a deeper issue.