Problem with low voltage at the generator

by Liz Stewart · 1 week ago 31 views 4 replies
Liz Stewart
Liz Stewart
Active Member
16 posts
thumb_up 1 likes
Joined Jan 2025
1 week ago
#19894

Had a similar headache last year with my Victron Multiplus-II and a cheap diesel genny — worth sharing in case others are going through the same.

The generator I was using (a Hyundai 6.5kW, no AVR) was throwing out voltage that wandered all over the place under load — sometimes dipping to 205V, occasionally spiking past 250V. The Multiplus just flatly refused to accept it as a valid AC source. Frustrating doesn't cover it.

What eventually sorted it:

  • Lowering the AC input low limit in VEConfig — I dropped mine to 180V as a starting point
  • Disabling UPS mode — this made a huge difference, the Multiplus became much less fussy about transfer timing
  • Increasing the AC input current limit gradually to avoid overloading the genny on startup

I didn't mess with country settings personally, but I've seen posts on the Victron Community forum where people running non-AVR generators in the UK have changed the frequency acceptance range slightly. Worth reading through if you're still stuck.

One thing I'd genuinely recommend — if your generator is running without an AVR and you're regularly relying on it for backup, just get an AVR-equipped machine. The Fogo units people mention seem decent but I can't speak from direct experience. Hyundai, Stephill, and Honda EU series all behave much more predictably with inverter-chargers in my experience.

Anyone else found specific VEConfig settings that work well with AVR-less generators in a UK setup? Curious whether the country standard tweak actually helps or just masks a deeper issue.

Spider
Spider
Active Member
38 posts
thumb_up 24 likes
Joined Aug 2023
1 week ago
#19922

@LizStewart this rings a bell from my narrowboat days — I ran a similar rig before switching most things over to solar.

The bit that caught me out wasn't just the AVR situation, it was the interaction between the Multiplus-II's UPS function and a wobbly frequency. Cheap gennies don't just sag on voltage — they hunt on Hz too, especially under variable load. The Multiplus sees that instability and goes into a kind of defensive crouch.

Worth checking your AC input sensitivity settings in VEConfigure. There's a "wide input frequency range" option that's off by default — enabling it bought me significantly more tolerance before the inverter started rejecting the generator's output entirely.

Didn't solve the underlying problem obviously, but it stopped the constant switching-out while I sorted a proper solution.

ExFirefighter
ExFirefighter
Active Member
44 posts
thumb_up 34 likes
Joined Jan 2024
1 week ago
#19953

@LizStewart what was the actual voltage range you were seeing at the generator output — was it dropping under load or fluctuating at idle too?

I ask because on my narrowboat setup I had a similar situation where the Multiplus-II was throwing low AC input alarms, but the root cause turned out to be a combination of weak AVR and undersized cable run from the genny to the inverter. Voltage drop across cheap 2.5mm² flex made a borderline situation into an unacceptable one.

Worth checking:

  • Input sensitivity settings in VEConnect — the Multiplus can be configured to accept a wider AC input range
  • Cable gauge and run length to the genny
  • UPS function enabled or disabled

Did you log the AC input voltage via the Cerbo or VRM portal? That data would tell you exactly what the Multiplus was seeing.

Curly
Curly
Active Member
16 posts
thumb_up 1 likes
Joined Apr 2025
1 week ago
#19964

@LizStewart — the no-AVR issue is a classic trap. I've seen the same thing manifest on my Victron Multiplus-II 24/3000 in the motorhome when I've occasionally borrowed a budget genny on site. The Multiplus's input voltage window is actually fairly tight by default — worth checking your assistants settings in VictronConnect and widening the AC input low/high thresholds if you haven't already. Mine was set to disconnect at 207V which caused repeated relay chatter under load.

Also worth noting: the Hyundai HY6500LEK does have an AVR on later production runs — worth checking your serial number against their documentation, because some early units shipped without it despite the spec sheet claiming otherwise.

@ExFirefighter's question about load-dependent voltage drop is the right one to answer first — that distinguishes a weak AVR from a genuinely undersized generator struggling with reactive load from the inverter's input stage.

Rocky Mender
Rocky Mender
Active Member
16 posts
thumb_up 2 likes
Joined Dec 2024
1 week ago
#19994

@LizStewart my garden office Victron nearly had a meltdown when I plugged in a similarly budget genny — turns out "6.5kW" on the sticker is doing a lot of heavy lifting as a number.