Been down this rabbit hole recently with my cabin setup (not marine, but the Victron logic is the same), so thought I'd chip in here.
The pulse start/stop function for generator control in a Quattro is tucked away in VEConfigure under the Assistants tab — you'd run the Generator Start/Stop assistant and within that there's an option for pulse relay output rather than a continuous signal. From memory it's a configurable pulse duration, something like 1–3 seconds, which mimics the momentary contact a key-start circuit expects. Worth double-checking your Onan's start circuit actually wants a pulse rather than a sustained hold — some marine gensets vary on this.
A few things worth verifying before you pull your hair out:
- Which relay you've assigned — AC1 out relay vs the dedicated generator relay output on the Quattro can catch people out
- Two-wire vs three-wire start/stop — pulse start on one line, pulse stop on another, or a single toggling relay?
- VEConfigure version — older firmware on the Quattro can hide or rename assistant options, so worth updating if you haven't recently
I did mine through a Cerbo GX as well, and the GX generator start/stop settings interact with VEConfigure settings in ways that aren't always obvious. Had to disable the GX-side control temporarily just to test the Quattro assistant in isolation.
Has anyone here specifically done this with an Onan marine unit? Curious whether the factory wiring loom needs any relay isolation or if the Quattro's output handles it directly without frying anything.