Bit of an odd one this, and curious whether others running Pylontech with a Multiplus-II have seen similar.
On my narrowboat I've got a Multiplus-II 48/3000 paired with 4x Pylontech US3000C batteries and a couple of Victron SmartSolar MPPTs. The Pylontechs are supposed to top out at 52.4V, but I've occasionally logged the effective charge voltage nudging past that — sometimes touching 53.8–54V briefly before settling back down.
Not quite the 54.4V some are reporting, but close enough to make me pay attention.
From what I can work out, it seems to happen when:
- The MPPTs and the MPII are both pushing charge simultaneously
- ESS is doing something clever (or not so clever) in the background
- The BMS hasn't quite communicated fast enough to clamp things back
I've got mine set up with DVCC enabled and the Pylontech talking to a Cerbo GX via CAN bus, which should let the BMS dictate charge limits properly. And most of the time it does. But there's clearly some lag or edge case where voltage creeps up temporarily.
Has anyone pinned down whether this is a firmware issue, a DVCC config problem, or just the nature of how ESS coordinates multiple charge sources?
Worth noting for those of us off-grid or on boats — we don't always have a stable grid reference for ESS to anchor to, which might be making things worse compared to a typical house install.
Would be interested to hear what firmware versions people are running on both the MPII and the Cerbo when this crops up.