Been mulling this one over since someone in another group mentioned running 10 modules in series on an RS 450/200 with Pylontech batteries.
The 8× float voltage rule is the bit that catches people out. Victron's own guidance says your max array Voc (corrected for lowest expected temp) shouldn't exceed 8× the battery float voltage. With Pylontechs floating around 53.2V, that's a ceiling of roughly 425V — which sounds generous until you start stacking high-Voc panels in a cold snap.
On my static caravan setup I'm only running a modest array through an MPPT 150/70, but I've been speccing a bigger garden office system and nearly made this exact mistake. Winter Voc on some of the newer higher-efficiency panels (thinking AIKO territory, 40V+ Voc per module) can creep up fast when temps drop to -10°C or below — rare in the UK but not impossible, especially up north.
With 10 modules in series at say 40.9V Voc, you're already at 409V before temperature correction. Add a cold morning and you could be nudging or breaching that 425V limit depending on your location.
Anyone here actually running 10S configs with Pylontechs and the RS 450/200? Curious whether people are:
- Dropping to 9S to stay safe
- Using temperature-corrected Voc calculations and accepting the marginal headroom
- Splitting into parallel strings instead
Would love to know what Fogstar or other Pylontech-compatible setups people have paired with this. Seems like 9S might just be the sensible call for UK installs given our temperature swings.