Finally got my shed office wired up last month and went through exactly this head-scratching exercise. Worth getting clear on a few things before you proceed.
First — is your supply coming from the house via an armoured cable (SWA)? If so, the armour itself can serve as the earth path back to the house CU, but you still need to check your main earth arrangement is up to scratch. Don't assume it just works.
The key question with a detached building is whether you're doing a TN-S arrangement (earth via the armour back to the house) or installing a separate earth electrode at the shed and running TT. Most domestic installs here in the UK end up going TT for outbuildings because:
- The earth fault loop impedance via a long SWA run can be too high for MCBs to trip reliably
- TT with an RCD + earth rod is often cleaner and more straightforward
If you go TT, you'll need a decent earth rod driven in (copper-clad, minimum 1.2m ideally deeper) and your consumer unit must have RCD protection on all circuits — a dual RCD board or RCBO per circuit.
Victron kit plays nicely with either arrangement if you're running any solar/battery into that office too, just worth noting.
Honestly though — if you're not confident on this bit, get a sparky to at least check and certify the earthing. The wiring regs (BS 7671) are quite specific on detached building supplies and an EICR will be needed if you ever sell.
What's your cable run like — how long and what size SWA did you pull through?