Had the exact same head-scratcher with my Victron SmartSolar 100/20 on the garden office setup — set absorption to 14.4V for my Fogstar AGM, watched VictronConnect smugly report 13.8V instead like it was doing me a favour.
Turns out there are a few culprits worth checking:
- Wire losses — Victron measures voltage at the controller terminals, not the battery. If your cable run is longer than a couple of metres with undersized wire, you're losing voltage before it even gets there. Add a battery sense dongle or use the Bluetooth sensing feature and it'll compensate properly.
- Temperature compensation — if you've got the temp sensor attached, it'll quietly adjust voltages downward in warmer weather. Worth checking what it's actually reading.
- State of charge logic — the MPPT will sometimes drop out of absorption early if it reckons the battery is full. Not always wrong, but worth cross-referencing with a decent battery monitor like a Victron BMV-712.
The Sunwind AGMs are Scandinavian spec'd — their 14.22V recommendation is a bit conservative compared to what most UK installers would set for a similar battery, but it should still be hitting that target regardless.
Anyone else running AGMs on a SmartSolar and finding the voltages drift seasonally? Wondering if this is more common than people realise once British "summer" temperatures get involved.