Bit of a rabbit hole this one, and I've been down a similar path with my motorhome setup so thought I'd chip in.
Running a pair of Multiplus II 12/3000s myself, originally with four 12V batteries daisy-chained. The uneven discharge problem nearly drove me mad — one battery doing all the heavy lifting whilst the others sat there looking smug. Took me an embarrassingly long time to realise the issue wasn't the Victrons at all.
The root cause in my case came down to cable lengths and connection points. When you daisy-chain, the batteries closest to your busbars see the load first. Physics, innit. I switched to a proper star topology — equal length cables from each battery to a central busbar — and the difference was immediate. Resting voltages across all four banks evened out considerably.
Worth also checking:
- Are all your SOK units running the same firmware? Mixed firmware can cause BMS communication quirks
- Are you using the Ve.Bus to monitor individual battery contributions, or just total bank voltage?
- What's your cable cross-section between batteries? Undersized interconnects cause resistance differences that compound over a discharge cycle
The SOK 314s are solid units — I nearly went Fogstar Drift before settling on a different chemistry — but they're still only as good as the installation around them.
Curious whether anyone's tried active balancers between units in a non-lithium-to-lithium config? I've seen some chat about it but nothing conclusive for this sort of parallel bank arrangement.
Would love to know how others have tackled this.