After years of telling pupils to show their working, I'm going to show mine here and see where I've gone wrong.
The static is on a site in North Yorkshire. Mains hook-up is unreliable — we lose power several times a year, sometimes for 6–8 hours. I'm not trying to go full off-grid, just keep the essentials running: fridge-freezer (~150W), a couple of lights, phone charging, and the central heating pump/controls (~80W). That's roughly 350–400W continuous draw, maybe 600W with the fridge compressor startup surge. I've got a modest 200Ah 12V LiFePO4 from Fogstar, which gives me a usable ~2kWh, so call it 5 hours of runtime at that load — which covers most of our outages.
My current thinking is a Victron MultiPlus 12/1200/50, wired between the incoming mains and the consumer unit. In passthrough mode it's invisible; on outage it switches to inverter within 20ms. The 50A charger would also top the battery back up quickly when mains returns. But I'm second-guessing whether 1200VA is comfortably enough headroom, or whether I should be looking at the 12/2000/80 instead despite the extra cost and slightly higher idle draw.
Has anyone here run a similar setup in a static? Specifically wondering whether the MultiPlus handles the heating pump startup without hiccup, and whether the 1200 is genuinely sufficient or if you'd always recommend oversizing the inverter on principle.