Been getting something similar with my Multiplus II (5000VA, 48V setup at the static caravan) and it's been driving me a bit mad trying to pin down the cause.
Mine does an occasional sharp relay click — sometimes in clusters, sometimes just a single one — and I initially thought it was the transfer switch doing something odd. Took me a while to realise it correlates pretty heavily with grid fluctuations, especially during stormy weather when the local supply here gets a bit wobbly. The unit seems to be constantly checking whether to hand off between grid and inverter mode, and each decision makes that click.
A few things worth checking if you're seeing the same:
- AC input voltage tolerance — tighten the range in VE.Configure so it's not constantly on the fence about accepting grid input
- ESS assistant settings — specifically the minimum SOC and the "keep batteries charged" mode interaction
- Cloudy days are interesting because if you're solar-dependent, the MPPT output fluctuating could be causing the ESS to constantly reassess load vs. generation
I've also noticed mine does it more when certain appliances cycle on and off — the fridge compressor kicking in seems to be a particular culprit, creates a momentary dip that the unit reacts to.
Have you connected it to VRM portal yet? The event logs are surprisingly useful — you can actually see what the unit thinks it's doing at the moment of each click. Made diagnosing mine considerably less guesswork.
Anyone else found specific settings that calmed this down? Curious whether tightening the AC input range is the usual fix or if there's something else people have tried.