Honestly this is one of those setups that makes me scratch my head a bit. Three phase from a 24v bank is a fairly awkward combination — the current draws at that voltage get eye-watering pretty quickly once you start pulling any real load.
Most of the three phase inverter options I've come across (Victron Quattro stacks, SMA Sunny Island multi-unit setups) really want to be sitting on 48v minimum, and a lot of the more serious kit prefers even higher — 96v or 120v DC bus territory. The maths just works out cleaner.
What's the actual use case here? If it's for three phase motors or machinery, there might be a simpler route depending on what loads you're running. A VFD off a single phase 48v inverter output can generate three phase for motor loads without needing to redesign your whole battery system.
If you're dead set on keeping the 24v bank, I'd be curious what capacity we're talking about. Fogstar Drift cells or something similar in a large parallel arrangement? Because the cabling and busbar situation alone at 24v trying to deliver three phase loads is going to be... interesting.
I've only ever run single phase from my own setup (48v, Victron Multiplus-II) so I'd genuinely welcome input from anyone who's actually done three phase off-grid in the UK — particularly whether you went with parallel inverters or a dedicated unit. There seem to be a few Chinese units floating around but I've not seen much real-world feedback on them.