Been through almost exactly this commissioning headache with my shepherd's hut setup last spring, so this might save someone some time.
I had a Cerbo GX refusing to see my MPPT and a Multiplus II — both were sitting there connected via VE.Direct and VE.Bus respectively, showing nothing in the device list. Turned out I'd made two separate mistakes:
VE.Direct cables — I'd used a third-party cable from Amazon. Looked fine, but the Cerbo simply wouldn't enumerate the MPPT. Swapped for a genuine Victron cable and it appeared immediately. Lesson learned the expensive way.
VE.Bus / MPPT firmware — The Cerbo's firmware was newer than what the Multiplus II expected. Had to connect a laptop with VictronConnect via Bluetooth, update the Multiplus firmware over MK3-USB first, then let the Cerbo pick it up. Order of operations matters here.
A few things worth checking methodically:
- Confirm each device shows in VictronConnect independently before expecting the Cerbo to see it
- Check the Cerbo's VE.Direct port assignments under Settings → System Setup — easy to have the wrong port mapped
- With Dyness batteries specifically, you'll need the correct CAN-bus profile set (usually CANbus BMS, 500 kbit/s on the GX)
- Restart sequence matters: batteries on first, then inverter, then let the Cerbo initialise
Has anyone had issues with the 450/100 MPPT specifically on newer Cerbo firmware builds? I'm curious whether the larger controllers behave differently to the 100/20s I've used before.