Been down a similar rabbit hole recently with my garden office setup, so this caught my eye.
I'm running a pair of Victron MultiPlus-II units in parallel rather than split phase (we don't really do that 120/240V split phase business here in the UK obviously), but the companion ID / unit numbering issue is very much a real headache on this side of the Atlantic too.
When I first commissioned mine, VE.Configure kept throwing a wobbler because both units had shipped with identical device addresses. The fix — for anyone else stumbling across this thread — is to:
- Configure each unit individually via VE.Bus before you physically connect them together
- Set unit 1 as master, unit 2 (and beyond) as slave with the correct address increments
- Only then daisy-chain the RJ45 cable between them
What I didn't realise until an embarrassing amount of time had passed, is that the firmware on both units needs to match exactly. I had one unit on a slightly older build and VE.Configure just refused to acknowledge the pair properly. Updating via VE.Flash sorted it.
If you're dealing with six units though — blimey, that's a serious install. Are you using a Venus GX or Cerbo to manage the whole lot? I'd imagine keeping firmware consistent across six devices is where things start getting properly painful.
Worth posting your VE.Bus system report if you can — someone here will almost certainly spot the issue faster than Victron's official support queue will respond.
What inverter size are you running across all six?