Been chasing a gremlin in my shepherd's hut setup for the past fortnight and wondering if anyone else has hit the same wall.
Running a Multiplus II 48/3000 with a 16s LiFePO4 pack and Fogstar Drift cells, managed through a JK BMS talking to Cerbo GX via CAN. Most of the time it's rock solid — genuinely one of the more satisfying builds I've done.
But occasionally, usually first thing in the morning when the BMS is waking up and the Multiplus is trying to initialise, I'm getting a VE.Bus Error 11 flagged in Venus OS. Specifically it seems to be hanging at Step 0 of the pre-charge sequence, then recovering on its own after a minute or two. No actual power loss, just the error sitting there in the notification log like a bad omen.
My suspicion is the BMS is a fraction slow to assert the DVCC charge voltage before the Multiplus decides something is wrong — but that's mostly guesswork at this point.
A few things I've already tried:
- Lowered the
Battery monitorscan delay in VEConfigure - Checked all the CAN termination resistors (both ends, 120Ω confirmed)
- Verified firmware is current on everything
It always clears itself, which makes me think it's a timing or handshake issue rather than anything fundamentally broken. But "it sorts itself out" isn't really good enough when you're relying on this for your only power source.
Has anyone got to the bottom of one of these? Particularly interested if you've solved it on a JK/Cerbo combination.