Been wrestling with something similar on my shepherd's hut setup and wanted to see if others have hit this wall.
Running a MultiPlus-II 48|3000|35 with a Cerbo GX, pair of Fogstar Drift 48V batteries, and a couple of SmartSolar MPPTs. When I tried enabling ESS mode and applied a grid code (G98 in my case, as required for any UK grid-tied configuration), the system threw a VE.Bus Error 11 — Relay Test Fault and refused to come up properly.
From what I've dug into so far:
- Error 11 is essentially the MultiPlus performing its internal relay self-test before connecting to the grid, and something in that sequence is failing
- It seems particularly sensitive to grid code selection — choosing the wrong regional standard (or having firmware mismatches between the Cerbo and the Multi) can cause the relay test to abort
- Some reports suggest the AC wiring configuration matters enormously here — neutral-PE bonding, earth loop resistance, all of it
My situation is slightly unusual because this is primarily an off-grid/emergency backup arrangement, so I'm not actually exporting to the grid. I only applied the grid code because VEConfigure was pushing me toward it for ESS functionality. Now I'm questioning whether ESS is even the right mode for a standalone shepherd's hut that occasionally sees a generator input.
Has anyone navigated this on a similar UK off-grid setup? Wondering whether:
- Dropping back to a non-ESS configuration avoids this entirely
- There's a specific G98/G99 firmware version known to behave with the 48|3000 unit
Keen to hear from anyone who's sorted this — particularly if