Been running a Fogstar Drift 100Ah in my garden office setup for about eight months now and honestly the Victron BMS has handled top balancing pretty well on its own. Let it do a proper absorption cycle every week or so and the cells stay reasonably tight.
That said, I did manually top balance before first use and I reckon that made a big difference to how well the BMS can keep on top of things ongoing. Starting from a good baseline matters.
A few things worth considering:
- Cell drift — if you're seeing more than ~20mV spread at the top, the BMS is working harder than it should
- Absorption time — are you letting it actually finish, or cutting it short?
- Temperature — my office drops quite low in winter and I noticed balancing got sloppier around 5°C
The Victron BMS balancer is passive and relatively low current (50mA on most units I think?), so if your cells are badly out it'll take ages to sort itself out. Manual intervention is quicker in that case.
What's your cell spread looking like at full charge? And which BMS exactly — the Smart BMS or one of the VE.Bus units? Makes a difference to what options you've got.
Curious whether others have found the passive balancing enough long-term or ended up adding an active balancer alongside.