Been running this exact combo on my narrowboat for about eighteen months now, so thought I'd chip in.
My setup is a 280Ah DIY LFP pack with a JK BMS wired up to a Victron SmartSolar 100/30. The key thing that took me a while to nail down was getting the charge profile right — LFP is unforgiving if you're sloppy with the absorption voltage.
I've got mine set at:
- Absorption: 14.2V
- Float: 13.5V
- Absorption time: 1 hour (fixed, not adaptive)
The JK BMS handles cell-level protection, but I still let the Victron do the heavy lifting on charge termination. What I don't do is rely on the BMS to disconnect as a normal part of the charge cycle — that's emergency-only territory in my book.
One thing worth mentioning for anyone on a boat or van — the VE.Direct cable running into VictronConnect is brilliant for keeping an eye on things remotely when you're away from the boat. Caught a dodgy connection on my positive busbar early because the yield figures looked off.
The bit I'm still fiddling with is whether to enable the tail current setting to end absorption early. Anyone here using that with JK BMS and found a sweet spot? I'm wondering if 2% of capacity is too aggressive for a 280Ah bank or whether I should push it closer to 4%.
Would love to hear how others have configured theirs, especially if you're running multiple panels in different orientations — that's my next headache.