Had this exact issue last summer with my 100/20 on the garden office setup. Drove me absolutely mental for weeks.
Turned out my battery voltage sensing was off — the MPPT was reading at the controller terminals rather than at the battery itself, so voltage drop across the cable was making it think the battery was fuller than it was. Switched to remote voltage sensing via the VE.Direct cable and a BMV-712 and it sorted it almost immediately.
A few things worth checking:
- Cable sizing — undersized cable between controller and battery causes voltage drop that fools the MPPT
- Absorption voltage setting — what have you got it set to? If it's too low, it'll hit float much sooner than expected
- Battery type profile — if you're on a Fogstar or similar lithium, make sure you're not accidentally running a lead-acid profile
- Temperature — Victron's temperature compensation can knock the absorption voltage down on warmer days, which shortens the absorption phase
Also worth checking whether it's actually a problem at all. If your battery is genuinely getting to 80-90% SOC fairly quickly (smaller battery bank, modest loads), hitting float "early" can be totally normal behaviour and not a fault.
What's your setup — panel wattage, battery capacity, cable runs? That'd help narrow it down. I've seen people panic about this and it's just their system working correctly, but I've also seen genuine configuration issues that waste a significant chunk of available solar.
Anyone else had the remote sensing fix work for them? Curious whether that's a common one or I just got unlucky with my initial install.