Spent three weeks convinced my Multiplus 2 (48V/3000VA) was faulty. It kept cutting out under load — washing machine mid-cycle, angle grinder, anything that pulled over 2kW for more than a few minutes. The fault log just showed "overload" but I was nowhere near the rated limit. Nearly sent the unit back to the supplier.
Turned out one of the busbars connecting my 16-cell 280Ah EVE LiFePO4 pack had a loose bolt. Resistance crept up enough that under load the voltage sag triggered the Multiplus's protection before the BMS even blinked. Tightened everything to spec with a torque wrench, cleaned the contacts, problem gone overnight.
What I've learnt: before you blame the inverter, check every connection between the battery and the unit. I'm talking busbars, fuse holders, Anderson connectors, all of it. A cheap clamp meter won't catch this — I only found it by measuring voltage at the Multiplus terminals under load and comparing it to voltage directly at the battery. The drop told the whole story.
Anyone else been down this rabbit hole? Curious whether this is more common with DIY packs than with something like a Fogstar Drift where the terminals are a bit more engineered.