Running a 48V system in my garden office with a 560Ah Fogstar Drift LiFePO4 battery and a Victron MultiPlus-II 48/3000 as the main inverter/charger. On grid-assist/ESS mode, the unit keeps cutting bulk charge short and jumping to float at around 80–85% SOC, even though absorption voltage is set to 57.6V and float at 54V. The battery BMS isn't tripping — I can see in VictronConnect that it's just the MultiPlus deciding it's done early.
Pretty sure this is the Tail Current setting biting me. It's currently at the default 4% of bank capacity, which on a 560Ah bank is ~22A. The solar and grid-assist together are pushing maybe 40A into the battery, so the charger thinks "current has tapered to near tail current" and declares it finished. Classic premature float. I've knocked it down to 2% (about 11A) as a test and it does seem to be holding in absorption longer now.
The bit I can't quite nail down is the interaction with ESS mode specifically. In a standalone charger setup it's straightforward, but ESS adds the grid setpoint logic on top, and I'm not 100% sure whether VEConfigure tail current behaves identically or whether the ESS assistant overrides it. Anyone running ESS on a similar-sized LiFePO4 bank who's dug into this?
Worth noting: I'm on MPII firmware 497, VEConfigure 3. Happy to share the .rvsc config file if useful.