Had exactly this with my Multiplus 24/3000 on the boat last summer. The washing machine motor startup surge was tripping the overload protection — even though the continuous draw was well within spec.
A few things worth checking:
Transfer switch delay — if you're on shore power some of the time, make sure the transfer is clean. Sometimes a hesitation there coincides badly with motor startup.
DC side voltage sag — this is the one most people miss. The inverter might be perfectly healthy but if your battery cables have any meaningful resistance, the inrush current causes a voltage dip that the BMS interprets as a low-voltage event and disconnects. Had this with my Fogstar cells before I replaced the 35mm² cabling with 70mm².
PowerAssist settings — if you've got shore power or a generator in the mix, check your PowerAssist threshold in VEConfigure. Sometimes it's set too conservatively and the unit cuts before it can assist properly.
What size Multiplus are you running, and is it the 12V, 24V, or 48V variant? The 12V versions are more susceptible to this because the current figures get enormous at lower voltages. A 2kW surge on 12V is 166A+ before you account for inverter efficiency.
Also worth logging with the Victron Connect app or a Cerbo GX if you have one — the event log often tells you exactly why it cut out (overload, low DC voltage, high temperature, etc.). That narrows it down instantly rather than guessing.
What does yours show in the history tab?