Had this exact issue last winter with my Multiplus-II 48/3000. Was seeing it drop to float at around 80–85% SOC, which was driving me nuts — especially when I'm trying to get a full charge before a run of overcast days.
After a fair bit of digging, the culprits for me were:
- Absorption voltage set too low — I had it at 56.8V for my Fogstar Drift LiFePO4 bank, bumped it to 57.6V and it made a noticeable difference
- Absorption time — I was using "adaptive" absorption, which can be very aggressive about cutting to float if it thinks the battery is full based on tail current
- Battery monitor calibration — my BMV-712 SOC was drifting, so the system thought it was fuller than it was
The fix that worked best for me was switching to a fixed absorption time (around 2 hours) and making sure the tail current threshold in the DVCC settings was appropriate for my bank size. The default 1A tail current is comically low for larger banks.
Worth checking whether you've got a BMS talking to the Cerbo via CAN-bus as well — if your BMS is broadcasting a charge current limit that's dropping off, the Multiplus will follow it down and tip into float prematurely. Victron's documentation on this is a bit sparse.
What battery chemistry are you running and what does your VEConfigure absorption time look like? That'd narrow it down considerably.