Had this exact issue with my Multiplus-II last summer on the static. Drove me absolutely mad for weeks.
Turned out my battery capacity settings were way off in VEConfig — I'd set the absorption time too short and the tail current threshold was cutting off bulk/absorption before the Fogstar Drift LiFePO4 cells were properly topped up. Once I bumped the absorption time up and lowered the tail current percentage, it sorted itself out almost immediately.
A few things worth checking:
- Tail current setting — if it's too high (say 4-5% of battery capacity), it'll trigger float prematurely on lithium
- Absorption voltage — make sure it matches your battery spec exactly, not just a generic lithium profile
- Battery capacity entered in VEConfig — if this is wrong, all the time-based calculations go sideways
- Temperature compensation — if you've got a sensor fitted, a warm battery can push it toward float faster than expected
Also worth connecting via VictronConnect or VRM if you've got it set up, and watching the charge cycle in real time. The graphs make it dead obvious where it's bailing out early.
What battery are you running? LiFePO4 behaves quite differently to AGM here, and some of the default Victron profiles still lean toward lead-acid assumptions. Worth checking whether you're on a custom lithium profile or just a tweaked default.
Anyone else had this with particular battery brands? Curious whether it's more common with certain BMS configurations cutting communication with the Multiplus.