Mine did this for about three weeks until I realised I'd set the input current limit so conservatively that a kettle basically sent the Multiplus into a panic and it threw its hands up like a Victorian fainting at the sight of an ankle.
A few things worth checking:
- Input current limit — if it's set too low, the Multiplus will passthrough rather than assist, which defeats the whole point
- AC input voltage thresholds — if your grid/hookup supply is a bit wobbly, it'll drop in and out; worth logging it on the Cerbo if you've got one
- ESS vs Inverter-only mode — are you running ESS? Because the assistant settings in there can cause some interesting behaviour during the day when SOC targets get confused
What's your battery situation — Fogstar or similar lithium, or AGM? Because if your BMS is sending a wonky signal over VE.Can or VE.Direct, the Multiplus sometimes sulks and decides grid is safer.
Also worth downloading VictronConnect and having a look at the alarm history — mine showed a "high DC ripple" warning I'd completely missed, which was the actual culprit (dodgy battery connection, embarrassingly).
Happy to dig into specifics if you post your config — there's usually a mundane explanation hiding behind what feels like the Multiplus having an existential crisis.