Victron Multiplus keeps switching to passthrough during the day - anyone else had this?

by Wonky Sparky · 17 hours ago 10 views 2 replies
Wonky Sparky
Wonky Sparky
Active Member
12 posts
thumb_up 5 likes
Joined May 2024
17 hours ago
#30080

Been following this thread with interest because I had almost the exact same issue last summer with my Multiplus II 3000. Took me ages to nail down what was causing it.

In my case it turned out to be the battery voltage dropping just enough during a cloud pass to trigger the low voltage passthrough threshold — even though the SOC looked fine on the Cerbo. The voltage sag was only momentary but the Multiplus was reacting to it faster than the BMS could communicate the actual state to the system.

A couple of things worth checking:

  • What are your DC input low/cutoff voltage settings set to in VE.Configure? Mine were left at defaults which were way too conservative for my Fogstar Drift LiFePO4 cells
  • Is your battery cabling adequate? Even slightly undersized cable can cause enough voltage drop under load to fool the unit
  • Are you on the latest firmware? There were some passthrough-related quirks fixed in more recent Multiplus II firmware

What battery type are you running and how is the system monitoring SOC — is it BMS-controlled or using the Victron shunt? That detail seems to make a big difference in how the Multiplus behaves.

Also curious whether it's happening at a consistent time of day or truly random? Mine was almost always around midday when the inverter load was highest, which was the clue that eventually pointed me toward cable resistance as part of the problem.

Would be good to hear what others have found — this seems to come up fairly regularly and there doesn't seem to be one definitive answer anywhere.

ExTrucker73
ExTrucker73
Regular
99 posts
thumb_up 33 likes
Joined Nov 2023
11 hours ago
#30111

@WonkySparky don't leave us hanging mate, what was causing it?! 😄

I've been having something similar on my motorhome setup — Multiplus 12/3000 — where it drops to passthrough seemingly at random during the afternoon. I think it might be battery temperature related (lithium cells getting warm in the sun) but I'm not certain.

Few things I've been wondering:

  • Was yours throwing any alarms in VictronConnect?
  • Did you check the DC input low voltage settings in VEConfigure?
  • Any chance it was a dynamic current limiter issue if you're on shore power?

Would love to know your fix before I start poking around blindly. My setup is also my emergency backup so I'm a bit nervous about changing settings without knowing what I'm doing!

Borders Nomad
Borders Nomad
Active Member
20 posts
thumb_up 1 likes
Joined Sep 2024
1 hour ago
#30146

@WonkySparky finish your sentence, man! Classic forum cliffhanger.

My money's on the DC input low voltage alarm triggering passthrough prematurely. Had the exact same phantom switching on my static van setup last spring — Multiplus kept deciding the batteries were dying at 2pm on a sunny day.

Turned out my battery voltage sense wires had a dodgy crimp, so the unit was reading maybe 0.4V lower than actual. Perfectly healthy 52V lithium pack, Multiplus thought it was seeing 51.6V and panicked itself into passthrough.

Worth checking:

  • VE.Configure → look at your actual logged voltage during the switchover moments
  • Physical sense wire connections at the battery terminals
  • Whether you're running Fogstar or similar LiFePO4 — some cheaper BMS units throw a brief voltage sag under load that confuses Victron's protection thresholds

Check your VRM portal logs first. The answer's usually sitting right there.