Mine did exactly this for about three weeks before I finally admitted it wasn't "sorting itself out" 😅
Nine times out of ten it's the AC input voltage dropping below your lower threshold — Victron's default is quite conservative and if your grid supply is a bit wobbly (mine in the garden office runs off a long cable from the house, so voltage drop is real), it'll flip to passthrough faster than you can say "why is my laptop on mains again."
Few things worth checking:
- VE.Configure / VEConfigure 3 → AC Input tab → lower your minimum input voltage (carefully, mind)
- Check your cable sizing — I was losing nearly 8V over a dodgy extension run before I rewired properly
- Look at the ESS assistant settings if you're running ESS; the "sustain" voltage might be kicking in earlier than you think
- Firmware — are you on the latest? My Multiplus II had a weird passthrough quirk that a firmware update quietly fixed
Also worth chucking Victron Connect open during an episode and watching the live data — you'll see exactly why it's switching. The VRM portal graphs are your best friend here if you've got a Cerbo or Venus GX logging everything.
What's your battery state of charge when it happens — is it consistently around the same percentage? That'd point toward SOC-based switching rather than a voltage issue.
Tagging in anyone who's wrestled with ESS on a garden setup — curious if others have seen this seasonally as the grid gets grumpier in winter.