Had this exact issue with my Multiplus-II last summer. Drove me mad for about two weeks before I tracked it down.
In my case it turned out to be the DC input low shutdown voltage set too conservatively. The Multiplus was deciding the battery was "too low" and dropping to passthrough to protect it — even though the SOC on my Cerbo was showing 40%+. The voltage sag under load was triggering it.
A few things worth checking:
- Battery type configuration — if it's set to AGM but you're running lithium (Fogstar Drift in my case), the voltage thresholds will be completely wrong
- DC input low restart/shutdown settings in VEConfigure — these are separate from your MPPT settings and often get overlooked
- ESS assistant if you're running it — there's a "minimum SOC" setting that can cause passthrough behaviour that looks identical to a fault
What's your battery chemistry and what does the DVCC screen show when it switches over? Also worth checking the VRM logs if you've got a GX device — the passthrough events should show up clearly and you can see exactly what voltage/SOC triggered it.
Is this happening at a consistent time each night or seemingly random? Consistent usually points to a threshold being hit, random could be a communication issue between the BMS and the Multiplus.
Worth posting your VEConfigure screenshot if you can — someone here will spot it quickly.