Had this exact issue on my shepherd's hut build last winter. Multiplus II 24/3000 was dropping to passthrough somewhere between 2-3am most nights, then picking back up once the sun hit the panels.
After a fair bit of head-scratching I traced it to the low battery voltage threshold being set too conservatively in VEConfigure. The default settings were cutting out earlier than they needed to, especially with the voltage sag you get under load overnight. Temps were dropping to near freezing which wasn't helping the battery readings either — I've got Fogstar Drift lithium cells and they do behave differently once it gets cold.
A few things worth checking:
- DC input low shut-down voltage — is it set appropriately for your battery chemistry?
- Are you running a BMS? If so, is it possibly triggering the Multiplus via the VE.Bus signal?
- Check VRM overnight logs if you've got a Cerbo GX — the SOC and voltage graphs usually tell the story pretty clearly
Also worth looking at whether you've got any parasitic loads quietly draining the bank more than you expect. I added a simple clamp meter overnight and found my water pump control board was pulling more than I thought.
What battery setup are you running and what does your overnight load look like? Makes a difference to where the fault might sit. Curious whether others have seen the BMS comms triggering this — I've read a few threads suggesting that's a common culprit but never fully confirmed it on my own setup.