Had exactly this on my narrowboat setup last winter — turned out my battery voltage sensing was lying through its teeth because of a dodgy connection on the sense wires, not the cells themselves.
Few things worth checking:
- Remote sense wires — if your Multiplus is using them, a high-resistance joint will report a lower voltage than reality, especially under load
- VE.Bus Smart Dongle or Cerbo — worth checking if the alarm correlates with any decent load spike, which would suggest the DC ripple threshold is being tripped rather than actual low voltage
- DVCC settings in VeConfigure — if you've got a BMS talking to the Multiplus and the BMS is reporting a slightly pessimistic SoC, it can trigger the alarm even when individual cells look perfectly healthy on a separate monitor
Also worth pulling up the VictronConnect history and checking whether the logged low voltage events match what your cells were actually doing at that timestamp — nine times out of ten there's a 0.2–0.3V discrepancy that tells the whole story.
What BMS are you running and is this a Fogstar/EVE cell build or something else? Makes a difference to how the Multiplus is interpreting the data it's getting.
Fairly confident this is a comms or sensing gremlin rather than your cells throwing a wobble — the Multiplus is dramatic like that. 🔌
Anyone else had the false alarm saga? Would be good to get a few more data points in this thread for future searchers.