Had this exact same gremlin with my garden office setup last year. Turned out my battery voltage sense wires had a dodgy crimp — Multiplus was reading voltage at the inverter terminals rather than the actual battery, so voltage drop under load was triggering the alarm even though the cells themselves were perfectly happy.
Worth checking a few things:
- Voltage sense wiring — if you're not using the dedicated sense terminals, the Multiplus just reads at its own DC terminals which can be misleading under load
- DC cable sizing — undersized cables will cause enough voltage drop to fool it
- VE.Configure settings — specifically the DC input low shutdown and low restart voltages, easy to accidentally have these set too conservatively
Also had a mate who had this with a Fogstar Drift battery — BMS was briefly sagging the voltage on high loads before the cells had actually dropped, so the Multiplus saw a genuine dip even though resting voltage was fine. Turned out he needed to tweak the low battery threshold slightly.
What battery are you running and what are your current DC input voltage thresholds set to in VE.Configure? That'd narrow it down a lot.
Anyone else seen this with particular BMS configurations worth flagging here?