Had something similar on my motorhome build last spring. The Multiplus was screaming low battery but my BMV-712 was showing 24.8v which seemed perfectly healthy to me.
Turned out the issue wasn't the resting voltage at all — it was voltage sag under load. The moment the inverter tried to push any serious wattage through, the voltage at the battery terminals was dropping way below what the BMV was reading at its sense wires. In my case I had a dodgy connection on one of the busbars that was creating resistance and causing a localised drop.
A few things worth checking:
- Cable sizing — are your cables adequately rated for the load? Undersized cables cause voltage drop under load
- Connection quality — torque check every terminal, look for corrosion or loose crimps
- Battery internal resistance — if you're running AGMs that have done some mileage, they can look fine at rest but sag badly under load
- Low battery cut-off settings — worth double-checking what threshold you've set in VictronConnect, sometimes it's configured more conservatively than you'd expect
What battery chemistry are you running and what loads are you putting through it when the alarm triggers? Also, are you monitoring with a Victron BMV or shunt, or just going off the Multiplus display itself?
Would be useful to know if the alarm happens instantly under load or after a sustained period — that changes the diagnosis quite a bit. Others on here will have more experience with specific Multiplus configurations than me so hopefully someone can chip in.