Had almost the exact same thing driving me mad last winter on the boat. Turned out my battery settings in the Multiplus weren't matched to my actual bank — I'd upgraded to a Fogstar Drift 200Ah LiFePO4 but the absorption and float voltages were still dialled in for the old AGMs. The Multiplus was reading voltage sag under load and panicking, even though the cells were absolutely fine.
Few things worth checking:
- Battery type settings in VEConfigure — make sure you've told it what you're actually running
- DC input low shutdown/restart voltages — these are often left at factory defaults which are way off for lithium
- If you've got a BMV-712 or SmartShunt, check whether the Multiplus is taking SOC from that via VE.Bus or just making its own assumptions based on voltage
The voltage-based SOC estimation is notoriously unreliable under load, especially in cold weather when internal resistance goes up. On the cut, I was getting false alarms every time the inverter kicked in for the kettle.
Once I set proper DVCC settings through Venus OS on a Cerbo GX and let the BMS talk properly to the Multiplus, the warnings stopped almost entirely. It's all about getting the system to trust one source of truth for SOC rather than having components second-guessing each other.
What does your setup look like — are you running a GX device, and what battery chemistry? Makes a big difference to where you'd start digging.