Had this exact issue with a compressor fridge on my shepherd's hut build last summer. The startup surge was absolutely hammering my Multiplus 12/3000 — kept triggering the overload protection even though the freezer's running wattage is only around 150W.
A few things worth considering:
Is it the PowerAssist or transfer switch relay clicking, or a full shutdown? There's a difference between a momentary hiccup and the unit actually tripping to fault.
Compressor startup surges can be brutal. Older chest freezers are particularly bad — the capacitors and motor windings degrade over time, so the inrush current gets worse as the unit ages. Some older units can pull 6-8x their running current for that half-second kick.
What I did that helped:
- Enabled the ESS assistant and tweaked the dynamic current limiter settings in VictronConnect
- Added a soft starter — there are cheap 16A ones on Amazon that genuinely work
- Made sure my battery cables were properly sized (voltage sag on startup was making it worse)
Worth checking what your battery setup is too. If you're on a smaller LiFePO4 pack with a BMS that has aggressive current limits, the BMS might actually be the culprit cutting out rather than the Multiplus itself.
What size Multiplus are you running and what's your battery bank? That'd help narrow it down. Others on here with van conversions and static caravans have had similar — it's a surprisingly common thread.