Been following this thread with interest because I had almost identical issues when I first tried running a chest freezer off my Multiplus II 3000.
The compressor startup surge was absolutely hammering the inverter — tripping the overload protection within seconds every time. Turned out the freezer's motor was drawing something like 4-5x its running current on startup, which is apparently completely normal for older compressors but brutal on inverters.
Few things that actually helped in my situation:
- Enabling the PowerAssist feature — made a noticeable difference
- Adjusting the transfer switch settings in VictronConnect (the AC input current limit was set too conservatively)
- Checking whether ESS assistant was affecting how the unit handled surge loads
Worth asking — how old is the freezer exactly? Older compressor motors tend to have much higher locked-rotor currents than modern inverter-driven compressors. If it's pre-2010, you might be fighting a losing battle depending on your battery bank's internal resistance too. A weak battery can't deliver the surge current fast enough, which makes the Multiplus work even harder.
Also, what's your DC cable sizing like? Undersized cables introduce enough resistance to cause voltage sag during that startup spike, which can trigger the low voltage protection rather than the overload protection — easy to confuse the two.
Has anyone here actually measured the startup surge current on older chest freezers? Curious what figures people are seeing. Would a soft-starter like the Micro-Air EasyStart even be compatible with a compressor-type freezer, or is that purely an air conditioning thing?