Had this exact issue with my shepherd's hut setup last year. Well pump motors are brutal on startup — the inrush current can be 6-7x the running current for a split second, which is enough to trip even a decent inverter.
Few things worth checking:
- PowerAssist settings in VictorConnect — make sure it's properly configured for your battery bank size
- AC input current limit — if you've got shore power or a genny connected, this might be throttling things at the wrong moment
- Transfer switch delay — sometimes tightening this up helps
What size Multiplus are you running? The 2000VA struggles more with pump startups than the 3000VA in my experience. If you're borderline on capacity, it'll trip every time.
Also worth asking — is it a submersible pump or surface mounted? Submersibles tend to have worse startup profiles. Some people fit a soft starter inline (Sollatek do a decent one) and it completely sorts the problem. Mine used to trip constantly until I fitted one, now it barely blinks.
Battery side matters too — if your cells can't deliver the burst current fast enough, the Multiplus sees a voltage sag and panics. What are you running for batteries? Lithium handles it way better than AGM for this kind of load.
What does the Victron history log show as the fault reason? That'll narrow it down pretty quickly.